Scenario

A scenario is a case study performed on a network. It is characterized by a type (e.g., SteadyGas, Steady ACPF, QuasiDynamic ACOPF, DCUCOPF, etc.), a length (i.e., a starting and ending time), a definition of settings, controls, and constraints, and their behavior over time (i.e., how they change by means of events and profiles). The mathematical model describing the type of scenario can be either a simulation or an optimization problem.

Please, refer to the How-To "Create a Scenario in SAInt-GUI" for more details on how to develop your own scenario in SAInt.

The sections "Gas Scenarios", "Electric Scenarios", and "Thermal Scenarios" provide mode details on the specific type of scenario. The section "Scenarios and Hub Systems" describes the special case of combined systems.

1. General properties

A scenario has a set of specific properties editable via the scenario editor. The scenario editor can be accessed using the ESCE, GSCE or TSCE under the scenario tab. The type of button depends on the type of available networks (e.g., electric, gas, or thermal). All scenario types in SAInt have a set of identical general properties. Table 1 provides an overview of the general properties of a scenario. The following section describe more specific properties of a scenario.

Table 1. General properties of a scenario. The properties Info is editable.
Property Description

Network

Name of the network the scenario belongs to

SolverStatus

Current status of the solver for the active scenario (e.g., solved, failed, etc.)

Name

Name of the scenario

SceType

Type of the active scenario (e.g., DCUCOPF, etc.)

Info

Optional information the user can specify related to the active scenario

1.1. Initial condition properties

A scenario can be initialized using values coming from a previous solution or from user-specified values derived by properties set by the user or specified in the default property values. In case of an steady or quasi-dynamic ACPF scenario, the user can also specify if a flat or warm start is required, along with the set of parameters and initialization strategy or values.

Table 2. Properties for the initial conditions of the initialization of a scenario. All properties are editable.The list of properties covers all scenario types, and once a scenario is chosen, some properties may no longer be available.
Property Description

WarmStart

Warm start type for a AC power flow simulation. Available options are: "NO" for flat start, "ECON" for another scenario’s solution file (to be specified with InitialState), "REF" for using some REF event properties as initial guess, "REFDEF " for using some REFDEF event properties as initial guess, and "DCPF" for using the results of a DCPF simulation for the system.

WarmStartInput

Warm start inputs for a AC power flow simulation. The user can specify any combination of voltage angle, voltage magnitude, active power, reactive power and tap position. The default is to select all parameters.

InitialState

Name of scenario whose terminal state is used as an initial state for the active scenario. "NONE" is used as default initial state if no other scenario is specified.

To select the input properties for WarmStartInput, click on the three dots on the right of the cell specifying the values of the property. The "Editor for WarmStartInput " window opens and allows to select the desired combination of properties.

1.2. Chart properties

It is possible to specify the time interval of interest for charting the results of a scenario. The chart section of the property editor allows to define the chart time window (i.e., by specifying ChartStartTime and ChartEndTime) of all the plots generated for the active scenario. For example, if a scenario has a time window of 1 year, but the user is interested in a specific week, it is possible to specify the time interval and generate only charts displaying results only for that specific week. A different chart time step (ChartTimeStep) compared to the scenario time step can also be defined. Table 3 provides an overview of the properties of the chart section.

Table 3. Chart properties of a (quasi-)dynamic scenario. In steady state scenarios these properties are not available.
Property Description

ChartStartTime

Start time for all chart plots

ChartTimeStep

Time step for all chart plots. It can be different form the time step of the simulation or optimization.

ChartEndTime

End time for all chart plots

The default value for ChartStartTime is set to the scenario’s properties StartTime plus one TimeStep. This allows for removing from charts the initialization step of any simulation or optimization. The values for ChartTimeStep and ChartEndTime match the scenario time step and end time, respectively.

1.3. Profile properties

The dynamic behavior of many events in a scenario can be modulated by using profiles. The profile section of the property editor of the active scenario allows to fine-tune how profiles are used. The profile properties allows to decide if to use a common global start time for all profiles (GlobalProfileStartTime) and to specify the exact starting time (GlobalProfileStartTime). Alternatively, the GlobalProfileStartTime is overridden by the individual profile start time (PrfStartTime). For example, if the GlobalProfileStartTime is 01/01/2022 01:00 while the PrfStartTime is 01/01/2022 05:00 for a PSET event on an EDEM object, the profile will start according to the PrfStartTime if GlobalProfileStartTime is unchecked.

Furthermore, it is possible to use an average profile for an event in place of the original profile by checking the option AverageFlowProfiles. The AverageFlowProfiles replaces the profile values with a moving average computed between a pair of adjacent scenario time steps. For example, if the first three values of a profile are 240, 234, and 228, the average flow profile will be 240, 237, and 231. The first data point of a profile is never averaged. Table 4 provides an overview of the properties of the profile section.

Table 4. Profile properties of a scenario.
Property Description

UseGlobalProfileStartTime

Enables or disables the use of the global profile start time for all profiles. The default is to have the option checked (i.e., Boolean value set to true). If unchecked, each profile is applied based on the time specified in PrfStartTime.

GlobalProfileStartTime

Set the start time for all profiles included in the active scenario. The default value is to match the start time of the scenario. The option is considered only if UseGlobalProfileStartTime is set to true.

AverageFlowProfiles

Indicates if all flow properties (unit per time) with an assigned profile should use an averaged profile over the scenario’s time steps. The first data point of a profile is never averaged.

1.4. File Information

The section "File Information" of the property editor covers details concerning the version of SAInt used to create the scenario, the time of creation and the time the scenario was last modified, and, finally, the path to the scenario file on the computer. This section reports non-editable details.

1.5. Network

The section "Network" describes the network type, the network name, and the path to the network file. This section reports non-editable details.

1.6. List of Objects

The section "List of Objects" allows the user to see and modify certain object sets related to the scenario. the list of profiles associated with the active scenario.

Table 5. List of objects entries in the scenario Property Editor.
Property Description

ScenarioEvents

Editable list of the events in the active scenario. Properties of the list’s members can be edited, but events cannot be added or removed.

SimTimePoints

List of the simulation or optimization time steps. This is a non-editable object.

Profiles

List of the profiles associated to the scenario. Properties of the list’s members can be edited, but profiles cannot be added or removed.

1.7. Other properties

The property editor allows to access and modify other properties associated with the active scenarios. In the time section of the property editor, the user can modify the start time and the end time of the scenario, as well as the time steps. Or in the solver section, the user can review the main settings of the solver for the simulation or optimization problem addressed by the active scenario. Please, refer to the section "Gas Scenarios", "Electric Scenarios", and to the section "Thermal Scenarios" for more details.

2. Scenario events

A key component in a scenario is an "event". An event defines a change in the setting, control, or constraint of a property of an object in the network at a specific time during the execution of a scenario. An object in a dynamic scenario can have multiple scenario events, listed in the collection editor for scenario events. In a steady state scenario objects are generally associated to one event of each type. The user can visualize and modify events either for a single object using the option "filter scenario event" or for the scenario using the scenario table. For a single object, the list of all events associated with the object is accessible by selecting the filter scenario events option from the context menu of the object. An event can simultaneously be created for multiple objects, as long as the objects are of the same type. An easy way to select objects of the same type is by using the model explorer window.

The list of all scenario events can be visualized from the event table, accessible using the EEVT, GEVT or TEVT under the scenario tab. An example of an instance of the "collection editor" and of an "event table" is shown in Figure 1 and Figure 2.

Please, refer to the How-To "Create a Scenario Event in SAInt-GUI" for more details on how to add your own set of events to an active scenario in SAInt.

events collection editor
Figure 1. Example of a collection editor for an XGEN object.
events table
Figure 2. Example of an electric scenario events table.

In the "event table", similar to the property editor and other windows in the SAInt-GUI, all text in blue can be edited by the user, while all text in black is fixed and can not be changed.

There are four scenario events categories common to all types of networks: set point, constant-updating, state, and constraint events. For electric networks, SAInt has a fifth category of events the average event. All scenario events are characterized by a common set of properties described in Table 6.

Table 6. List of the properties of all types of events.
Property Description

StartTime

Start time of the scenario event. For steady state scenarios, the value is set to the start time of the scenario. For dynamic scenarios, the user can specify the event start time by editing the property StartTime in the property editor or in the events table. The user can edit the prefilled value of an event (set to the scenario start time) or compose the value using the widget from the drop down button on the right of the cell.

Parameter

Scenario event parameter (e.g., PSET, QSET, etc.). Events depend on the object type.

Value

The scenario event value can be either a numeric value or an arithmetic expression. If a profile is assigned to the event, the value is used to scale the profile value at a specific time (e.g., 5, -3.2, EDEM.NAME.PSET, etc.).

Unit

The unit of measure to be used for the value of the event. This unit can be different from the default units of measure for the project. A drop-down menu allows selecting a different unit within the same unit type.

Active

Indicates if a scenario event is active (i.e., true) or inactive (i.e., false). Inactive events are not evaluated during the execution of the scenario.

ProfileName (Profile)

Name of the profile assigned to the scenario event

UsePrfStartTime (UsePrfStartTime)

Indicates if the profile start time defined for the event should be used instead of the global profile start time defined for the scenario

ProfileStartTime (PrfStartTime)

Start time of the first data point of the assigned profile. The default is to have the same global start time for all events in the active scenario. It could be modified on an event base by the user.

InterpolateProfile (InterpolatePrf)

The user can specify if an event value is modified by a profile only at the exact moment specified by the profile or for any time point where the profile is not defined. In this case, the profile is interpolated. It is a Boolean value with a default set to true.

AverageProfile (AveragePrf)

Indicates if profile values should be averaged over a scenario time step. The default is set to false. The option is considered only if InterpolateProfile (InterpolatePrf) is set to true.

UsedPrfInterpolation

Defines which profile interpolation type is used for interpolating the data points included in the profile. If no profile is assigned to the event, the value is "NOPRF". Other accepted values are: "POINT" for no interpolation between two data points, "STEP" for step interpolation, "LINEAR" for linear interpolation, and "CUBIC" for cubic splines interpolation. The interpolation allows to have a different time granularity between profiles and simulation.

Condition

Logical expression returning a true or false value. A script editor can be accessed to evaluate the expression.

Evaluation

Evaluation type for the logical expression defined for the condition property. Default value is "NONE". Accepted values are: DoIFTrue, DoIFFalse, DoUtilTrue, and DOUntilFalse. The expression is evaluated if it is true or false, or until the condition is true or false.

Name

Name of the object to which the event is associated

ID

Unique identification code for the object to which the event is associated

Info

Optional information defined by the user for the event

ObjType

Code of the type of object to which the event is associated

  • StartTime is only applicable to dynamic or quasi-dynamic scenarios.

  • If the profile is assigned to an event, the Value is scaled by multiplying by the profile weight for the active time step.

  • An event without a profile applies only at the StartTime and after that it is constant.

  • Some properties for an event may not be present in the scenario table. Use the "choose columns" or "show all columns" option to display the missing properties.

2.1. Set point event

A set point event is a desired value prescribed for a variable in the mathematical model describing a scenario. Figure 3 shows an example of a set point event for the penalty price (PSETPRC) of an electric demand (EDEM) object.

set point event
Figure 3. Example of a set point event in the case of an electric demand (EDEM) object.

2.2. Constant-updating event

A constant-updating event uses a profile to update the value of an object property for every timestep. Figure 4 shows an example of a constant-updating event for the power set point (QSET) of a gas demand (GDEM) object. The profile associated with the event has as name "PROFILE1" and it uses a cubic interpolation for time steps between profile points. Data interpolation is active, and the start time is set to the global scenario start time.

constant updating event
Figure 4. Example of a constant-updating event.

If the data points of a profile are less than the scenario time steps, profile data is interpolated by default.

2.3. State events

The state events have three types:

ON event

An ON event indicates that the network object is active and working. The solver is forced to include the object in the simulation/optimization. Figure 5 shows an example of an ON event for a solar generator (PV) at the time step 07/09/2022 00:00. The ON event is different from the status InService, because it the equation of the object is incorporated in the mathematical problem. When InService is "FALSE", the equation is not considered, the problem is simpler, and no events can be associated to the object.

on event
Figure 5. Example of an ON event.
OFF event

An OFF event indicates that the network object is out of service. The solver is forced to exclude the object from the simulation/optimization. Figure 6 shows an example of an OFF event for a solar generator (PV) at the time step 01/01/2022 00:00. In (quasi-)dynamic problems other events may be associated to the object at different times.

off event
Figure 6. Example of an OFF event.
ONOFF event

An ONOFF event indicates that the network object can be put back in service. The solver is evaluating if the object should be included or excluded in the simulation. Figure 7 shows an example of an ONOFF event for a fuel generator (FGEN) from 12/01/2022 00:00.

on off event
Figure 7. Example of an ONOFF event.

2.4. Constraint events

A constraint event sets the upper and lower limit of a variable. Figure 8 shows an example of a constraint event for the available capacity of a fuel generator (FGEN) from 10/01/2022 01:00.

constraint event
Figure 8. Example of a constraint event.

2.5. Average events

An average event creates an additional constraint on an electric object, which limits the average value of the object property over the time horizon of the scenario in the electric network. The averaging period of the event is defined from the following timestep after the event start time until the end time horizon. Additionally, an averaging period can be limited if another event is defined during this period. The average events have three sub-categories:

PAVG event

A PAVG event defines an average constraint on the active power (P) of an electrical demand object (EDEM) for the defined averaging period. Figure 9 shows an example of a PAVG event to constrain the active power of the electrical demand object during a 24-hour time horizon. In this example, the averaging period is from 18/07/2022 01:00 until 19/07/2022 00:00.

average event 001
Figure 9. Example of a PAVG event.
FAVG event

A FAVG event defines an average constraint on the fuel consumption rate (F) of a fuel object (FUEL) for the defined averaging period. Figure 10 shows an example of a FAVG event to constrain fuel consumption of the fuel object during a 120-hour time horizon. In this example, the averaging period is from 18/07/2022 01:00 until 23/07/2022 00:00.

average event 002
Figure 10. Example of a FAVG event.
AvgUpBound and AvgLowBound event

An AvgUpBound and AvgLowBound, also called multi-temporal constraints, are average events which define an upper and lower average constraint on the value of an electric variable (EVAR) for the defined averaging period. Figure 11 shows an example of an AvgUpBound event to constrain the active power of a set of hydro generators (HGEN) objects during a set time interval. In this example, the averaging period is from 18/07/2022 07:00 until 18/07/2022 19:00.

average event 003
Figure 11. Example of an AvgUpBound event.

3. Scenario profiles

A profile is a collection of temporally equidistant data points. Profiles are assigned to object properties through events. The processing of profile data points is based on the specified profile settings. A profile can be applied to multiple events. In Figure 12, the profile "PRF_AT_DEMAND" is applied to the active power set point (PSET) of an electric demand (EDEM) and to the minimum value (MinVal) required by an ancillary service (ASVC).

multiple profile events
Figure 12. Example of use of a single profile with multiple events.

The list of all profiles associated with the scenario can be visualized by the "profile table", accessible using the EPRF or GPRF under the scenario tab. As shown in Figure 13, the "profile table" is separated into three sections:

  • [1] "profile description table" displays the list of all the profiles and their properties.

  • [2] "profile data table" provides the selected profile’s mean and deviation data points list. Deviation data is only used for stochastic profiles.

  • [3] "profile chart window" visualizes the selected profile’s data points against the scenario time window.

profile table
Figure 13. Example of electric scenario profile table.

Table 7 provides an overview of all relevant properties of profiles.

Table 7. Profile properties.
Property Description

Name

Name of the profile

Info

Additional user specified information related to the profile

ProfileType

Type of the profile. SAInt accepts either deterministic or stochastic profiles. In deterministic profiles, the default type, the data points are specified and unchanged during the simulation. In stochastic profiles, data points are randomly generated each time a scenario is executed.

TimeStep

The time interval between two consecutive data points. The unit of measure is specified in the project settings.

Interpolation

The interpolation type used when generating profile values between two data points. Available options are linear (default), cubic, and step interpolation.

BaseDev

The standard deviation applied to all data points in stochastic profiles. Only used if UseBAseDev is selected.

MaxVal

The upper bound for profile values. The default value is infinite.

MinVal

The lower bound for profile values. The default value is negative infinite.

DevAtMax

Enables or disables the use of the standard deviation if the mean of the profile data is equal to MaxVal

DevAtMean

Enables or disables the use of the standard deviation when generating profile values for time points equal to the profile data point. If disabled, the deviation is only applied for profile time points where interpolation is required.

DevAtMin

Enables or disables the use of the standard deviation if the mean of the profile data is equal to MinVal

Distribution

Indicates which probability distribution function to use when generating profile values for a stochastic profile. Options are uniform (default), normal, or exponential distribution.

Duration

Indicates how profile values generated for time points outside the profile time window should be treated. The profile time window is derived by multiplying the time step by the number of data points. Available options are periodic (default), constant, and stop. Option periodic repeats the profile. Constant uses a constant profile value equal to the last data point value. And stop sets the profile value to zero.

Points

Number of data points in the profile

Sign

If enabled negative profile values are considered, otherwise negative values are set to zero

UseBaseDev

Option to use the same standard deviation BaseDev for all data points. Default value is false (i.e., unchecked).

UseBounds

Enables or disables the use of MaxVal and MinVal as upper and lower boundaries when generating profile values. It applies to both deterministic and stochastic profile types.

ProfileDataPoints

Collection of profile data points. The user can add, edit, or remove points. This option is represented as a small, separated table in the profile table window.

Scenario

Name of the scenario to which the profile is assigned. This option is available in the property editor of a profile.

Please, refer to the How-To "Create a Profile in SAInt-GUI" and "Assign a Profile to an existing Event" for more details on how to use profiles in your scenario.

3.1. Profile type

SAInt accepts two types of profiles: deterministic and stochastic profiles. In deterministic profiles, the default type, the user must define a priori the value of all data points. Such figures are not automatically changed between the simulation. In stochastic profiles, data points are randomly generated each time a scenario is executed. New values are sampled based on the type of distribution selected (i.e., uniform, normal, or exponential), and on the specified mean and standard deviation. Figure 14 shows an example of a deterministic profile, while Figure 15 shows an example of a stochastic profiles using the deterministic as mean value and setting a uniform distribution with standard deviation equal to 20.

deterministic profile
Figure 14. Example of a deterministic profile.
stochastic profile
Figure 15. Example of a stochastic profile.

3.2. Profile distribution

Stochastic profiles are defined by specifying the mean and standard deviation value for each profile data point, along with the type of random distribution to be used from drawing random samples. SAInt allows the user to select one of the three distribution options for the Distribution property. We have:

Uniform distribution

It applies a uniform probability distribution;

Normal distribution

It applies a normal probability distribution;

Exponential distribution

It applies an exponential probability distribution.

3.3. Profile interpolation

The time granularity of a profile and of a scenario may differ. When a profile has a coarser granularity, the user can specify if and how to interpolate for any time step not present in the profile. All interpolation options generate profile values between two data points. Available options are:

Linear interpolation

It applies linear interpolation between data points. In Figure 16, daily fuel prices of natural gas are linearly interpolated to hourly scenario time steps.

linear interpolation
Figure 16. Example of linear interpolation.
Cubic interpolation

It applies cubic interpolation between data points. In Figure 17, daily fuel prices of natural gas are interpolated using a cubic model to hourly scenario time steps.

cubic interpolation
Figure 17. Example of cubic interpolation.
Step interpolation

It applies step interpolation between data points. In Figure 18, daily fuel prices of natural gas are interpolated using a step model to hourly scenario time steps.

step interpolation
Figure 18. Example of step interpolation.

3.4. Profile duration

The length of a profile is defined by the number of data points multiplied by the time step. When a scenario has a length greater than the one of a profile, it is necessary to extend a profile so as to cover the entire simulation or optimization problem. Available options for the Duration property are:

Periodic

It repeats periodically the profile. In Figure 19, the profile is only defined for 24 hours. After the defined values, the profile is periodically repeated based on the length of the profile or fractions (i.e., 24 data points).

periodic profile
Figure 19. Example of a periodic profile.
Constant

It creates a constant profile equal to the last data point value. In Figure 20, the profile is only defined for 24 hours. After the defined values, the profile is extended with a constant value.

constant profile
Figure 20. Example of a constant profile.
Stop

It sets the profile value to zero. In Figure 21, the profile is only defined for 24 hours. After the defined values, the profile is set to zero.

stop profile
Figure 21. Example of a stop profile.

4. Solver type

We have informally introduced the concept of "scenario" as a case study performed on a network composed by constraints, conditions, events and profiles. In mathematical terms, a scenario is the translation of the case study into a set of equations describing the dynamic of the system. In order to numerically solve such set of equations SAInt uses a dedicated computational engines or "solvers".

The user can select among two different solvers:

Pardiso

The name is short for "PARallel DIrect SOlver", which is a thread-safe software library for the solution of large sparse linear systems of equations on shared-memory multicore architectures (see Schenk, Gärtner, Fichtner, and Stricker, 2001). It is written in Fortran and C. It is efficient for large systems and it takes advantage of parallelism.

SparseLU

The solver implements sparse linear algebra techniques using a new algorithm for LU factorization on general sparse matrices (see Valero-Lara, Greenwalt and Vette, 2023). It is written in C++ and uses the Eigen library. It is good for addressing small to medium size problems. The implementation is not parallelized. This is the default solver used for simulation problems in SAInt.

KLU

KLU is a set of routines for solving sparse linear systems of equations. It is particularly well-suited to matrices arising in circuit simulation applications. It relies on a permutation to block triangular form, several methods for finding a fill-reducing ordering (variants of approximate minimum degree, and nested dissection), and a sparse left-looking LU factorization method to factorize each block. For details see Davis, T.A., and c, E. (2010) "Algorithm 907: KLU, A Direct Sparse Solver for Circuit Simulation Problems" published in ACM Transactions on Mathematical Software.

Despite the selection of "SparseLU" as default solver for SAInt, the user is invited to experiment with other options which may improve the computational time based on the size and topology of the network.

The solver type can be changed in the Property Editor when looking at a scenario by modifying the property LinearSolverEngine.

The "pivot not found" exception for a simulation scenario using any of the three linear solvers available in SAInt indicates an issue in the mathematical formulation of the problem (e.g., overdetermined equations, short circuit, parallel valves, or lines with zero resistance or impedance).

The SAInt solver tries to pinpoint which variable may be triggering the issue and identifies the associated equations, which can help the user troubleshoot their model.